I've got a situation with a electric range circuit in an older house home where I am getting 146v phase one to ground, 93v phase to ground on the other leg, and 48v on the ground to another earth ground. With the range plugged in when I test the voltage between the cord terminals on the range I get 240v between one leg and the neutral/ground terminal, and zero volts between the second leg and the same neutral/ground terminal. I get 245v between both legs. This is a 3 wire aluminum circuit with the braided ground. I've visually inspected the cable from the range receptacle to the panel except for a 5ft section that isn't visible and have seen no damage. I've replaced the 50amp breaker and a new receptacle as well to no avail. Everything else in the home is working fine, no flickering of lights etc.., that would be common if there was a neutral problem on the utility end. My next step would be a whole new homerun, but before I do that is there something else I could be missing?
Thanks