kloc5
- United States
- Controls Manager
Hello,
We are using a 10KVA single-phase 480VAC to 120VAC transformer for our automation equipment. However, we are center-tapping the secondary so that we can get 240VAC across both hot legs for some devices, and balancing the 120VAC devices between the two 120V circuits.
My question is about sizing the OCPD for the secondary. Since we will have two hot legs, do I treat this as two 5KVA transformers to 120VAC and size the fuses accordingly (60A fuses I believe)? Do the wire sizes need to be sized as if each hot leg had the total possible current if it was completely unbalanced (83.3A)? What about the neutral leg wire sizing, since it is the return wire for both hot legs, but still the maximum current possible remains 83.3A if I'm not mistaken.
Thanks for your help!