I would tend to side with the contractor.Was told by a contractor that he cannot put screws on the front of a panel board? Is this correct? Any Code citations would be greatly appreciated, Thank you! Picture as a reference, those screws holding the plate, is that allowed?
Same here, many, many, many times and more. If they didn't want us drilling holes for rivets or screws they should provide them from the factory so we can label them.We use rivets or screws to attach phenolic labels all of the time.
I share that opinion if it is indeed a problem.or, if needed to be bolted or screwed on they should have provided the holes at the factory in a place where they want the label to be in my opinion.
JAP>
Yeah this seems like a no brainer. How would drill two small holes in the cover change anything? I've seen many panelboard covers with field installed hasps and locks too.Same here, many, many, many times and more. If they didn't want us drilling holes for rivets or screws they should provide them from the factory so we can label them.
In the example pictured that plate, label, whatever you want to call it was installed at the factory, it is listed and approved as is.I would tend to side with the contractor.
If it's a label that should come from the factory it should either be a label of the stick on type, or, if needed to be bolted or screwed on they should have provided the holes at the factory in a place where they want the label to be in my opinion.
JAP>
Your picture is of a switch enclosure. Putting a machine screw into an enclosure cover not likely an issue but to put a screw into a panelboard that is not part of the listed product design might very well be a violation. The enclosure of a panelboard is not necessarily listed item and code does allow for alteration that doesn't compromise the integrity of the enclosure for stated purpose, ie in a NEMA 3 enclosure creating an opening that would compromise the water intrusion integrity in a wet area.Was told by a contractor that he cannot put screws on the front of a panel board? Is this correct? Any Code citations would be greatly appreciated, Thank you! Picture as a reference, those screws holding the plate, is that allowed?
But you can make holes for raceways, push buttons, selector switches, indicator lamps, panel meters, etc. and that it fine?I think putting screws through the front of a listed piece of equipment is arguably a violation. 110.3(B). You are modifying the equipment other than according to instructions. Surely small metal screws don't matter on the deadfront or cover of a switch or panelboard, but if you say that's okay then where do you draw the line?
All the signs and placards I've ever attached were adhesive backed.
The listing requirement is for manufacturers to comply with when they make the item. Now if it would create a major problem to make modifications that would likely be in the listed instructions, like my example earlier of drilling a hole in an explosion proof enclosure, that typically is a big no, no you generally will compromise the explosion proof characteristics of the enclosure if you do so. Not even a mounting hole or a hole for a grounding screw in that situation.
And therefore the installer cannot modify the equipment without instructions because then it might no longer comply.The listing requirement is for manufacturers to comply with when they make the item.
Additionally what sort of screw being referred to? The screws I've seen some guys try to use like self tappers, sheet metal or wood screws can and have caused damage to conductors by incidental contact of the sharp edge or points.
Not sure I've ever seen instructions giving me permission to punch holes for conduit entriesUm, no, it's not fine at all. Not unless the instructions make clear it's designed for that.
My statement was about listed equipment.
(Also generally no sane person makes holes for raceways in the front of equipment.)
The code enforces this with 110.3(B).
generally with XP enclosures you can only enter with raceways into hubs that are integral to the enclosure. There is no drilling to make another entry because AFAIK there is no "myers hubs" designed for this situation. You might be able to drill to add entries, but it will never be suitable for use in XP application againIf that were the case you could not attach a conduit (with a seal) to an XP enclosure.