For the purpose of counting "current carrying conductors" in a raceway, per NEC 310.15(B)(3)(a): When does the neutral carry only "the unbalanced current from other conductors of the same circuit" (310.15(B)(5)? I would guess that this applies to 2 or 3 pole dedicated equipment that requires a neutral. Any help is greatly appreciated.
Here is a simplistic example dedicated equipment.
A 240V appliance,
It has a couple of 120V loads, a clock, timer, lights etc. All one the one leg of the 240V. As well as its straight 240V load.
Now say you total load is 20A, your 240V loads are 15A and your 120V loads are 5A.
Your neutral will be expected to carry the 5A from the 120V load that is above the balanced 240V load. (The Unbalanced Current)
Now here's an example of how you might experience a MWBC (typical 2 hot 1 neutral receptacle loads) best described when it goes wrong. (Unintentionally created MWBC)
A 120V circuit
Someone splices neutral from 2 or more circuits together
Turn off power from one circuit the 2nd circuit remains energized, a load is applied to second circuit
The neutral of the de-energize circuit will still carry the split of the neutral current associated with the energized circuit (parallel neutrals)
Now a properly configured MWBC
2 loads one 15A the other 10A
If loads are present on both phases of the of the MWBC (series) some of the current used of the one side of the circuit will feed through to the other side (nature of alternating current) reducing current to the 5A difference. Current through one load into shared neutral then paralleled (like the multiple neutral above) into the other load and returning. (Alernating current) (15A - 10A =5A)
At any other time if only one load is applied (say the 15A) there is no means for the current of that load to return on the opposing hot leg so full amount of that current will return on the neutral (15A - 0A = 15A)
Now another faulty installation issue.
MWBC both on same phase.
One 15A load and one 10A (parallel) creates a cumulative of 25A because there is no alternating of the current flow (both on same phase to cancel some of that load) the neutral will have to carry the full load of both circuit or full 25A, overloading the normal conductor sized for the 15A presumed maximum load. (15A + 10A =25A)