Older VFDs did not do motor protection. Now it is Code and NRTL required.
The front end protection is to protect the power system against short circuits in the drive and to keep the drive components from launching out of the drive when they fail. Overload protection in the drive itself is that thermal temperature sensors shut it down if it overloads. Remember it is not a conductor…transistors are semiconductors with very little thermal mass. They melt and/or explode in milliseconds.
Some manufacturers have learned the hard way. They thought they could do short circuit protection in software and attempted it on large 20 Megawatt drive systems in Australia. To add insult to injury they also made a serious error by using RMS ratings of the transistors in a mostly DC applications. All the design errors were discovered 18 months later when the first drive transistors launched themselves through the cabinet doors. This happened on the CSIRO sponsored UDD project.
The drive protects the motor if you set it up properly. If you don’t the motor can be burned up. Usually the drive manufacturer makes you do this. They do things like set the FLA to 1 A and overload class to 10 and SF to 1.0. That way it trips on overload until you set it up properly. That’s for a Listed (not CE) VFD from somewhere other than China.