Fittings
Alwayslearningelec
NJ
Estimator
Anyone have example of what they'd use for this type of fitting? What is the difference between cast & malleable?
"Fittings for rigid steel conduit shall be of cast or malleable iron, threaded, and be
protected by hot dip galvanizing."
Also do they even make cast iron boxes with KO's( assuming slip holes they mean KO's)?
"Where rigid conduits enter a cast-iron box with slip holes, they shall be furnished
and installed with 2 locknuts and bushings made of malleable iron or steel,
insulated with bakelite molded and locked into the bushings, such as
manufactured similar in design, construction, and performance by OZ/Gedney
Company, A Division of Emerson type HBLG or approved equal."
Black.gas pipe is malleable, if I'm not mistaken.
I think the idea with the fittings is they must be threaded, not compression (which are steel)
It is specifying fittings for RMC though. Other than unions, hubs, conduit bodies and FS boxes (last two aren't really fittings in the NEC) about only commonly used fittings remaining is couplings, the RMC itself is threaded unless using a compression fitting.
For sure. And I know a conduit body is not a fitting technically, but that's what I had in mind
According to the listing standard conduit bodies are fittings and conduit bodies fit the code definition of a fitting.
From the UL Guide Information for "Conduit Fittings (DWTT)"
This category covers metallic and nonmetallic conduit fittings, such as connectors, couplings, conduit bodies, short-radius conduit bodies, expansion fittings, locknuts and sealing (liquid-tight) locknuts for use in the assembly of nonmetallic and metallic wiring systems.
The Product Standard is UL 514B, Standard for Safety: Conduit, Tubing, and Cable Fittings. The scope of that standard includes conduit bodies.
Interesting. Thanks
When buying fittings, I look everywhere for the product standard UL 514B, but I don't always find them! I prefer steel products! Although I often work in cosmetic surgery plastic practice, I like to choose and do home repairs myself!