Service cables goes to a meter outside and then from there it goes into the ceiling all the way to a 200AMP MCB panel inside in the middle of the small commercial building, that feeds the whole building. The distance between the meter outside and panel inside is probably around 40'. 230.70 (1) says the service disconnecting means shall be installed at a readily accessible location either outside or inside nearest the point of entrance. In this case, the interior panel is not near the meter and it is located somewhere in the middle of building. Local codes does not specify required distance nor does the NEC. Should I provide disconnecting means by the meter? such as enclosed circuit breaker?
Thank you