So this is a bit of a best practice question about the AC disconnect on the PV terminals of the transformer.
Referencing 2017 here are the abridged requirements:
Its never actually been an issue I've had to ponder that close simply based on circumstance of the actual install but I was just looking to labels and it clicked that we label PV disconnects as "may be energized from line and load terminals." Now, I think that's a CYA label that means little with a grid-tied inverter, there are numerous protections that say that inverter is not producing anything when there is no AC grid, the inverters aren't self commutating so with the exception of large PV systems with inductive reflections from the grid itself, the inverter isn't capable of creating its own frequency and voltage (it is a current source and without voltage produces neither current nor voltage), not to mention rapid shutdown which also removes the source of energy from the inverter as well. But I don't believe there is any labeling requirement noting that the transformer may be energized from both the primary and secondary side but would article 450.14 - should there be?
- (Art 690) Evaluate each winding as pri and sec. and apply protection as determined; if xfmr FLA exceeds PV FLA then no pri protection needed on PV side of xfmr
- (Art 450) Disconnecting means is required on transformer within line of site or remote if lockable and location is marked on transformer, (Art 240) no secondary disconnecting means is required if terminating indoors, if conductors are outdoors unlimited length to a secondary disconnecting means
- (Art 690) PV equipment must have an AC disconnecting means in line of site of PV, exception is remote operated where the device to operate is within line of site of the equipment