Don’t see anything clear in the code for installing a single(s) receptacle on a branch ckt. Do the same rules apply like in 210.21 B 3 that if there are more than one receptacle on a 20 amp ckt you can have 15 amp receptacle or 20 a receptacle on that ckt. So in this case a single or multiple single 15 amp receptacles on a a 20 amp circuit as long as there are 2 devices on that ckt is fine?

Also, is a single receptacle really only designed for a dedicated ckt like a fridge or microwave or is it acceptable on a branch ckt where you want to limit any other loads from being plugged in?
 
Don’t see anything clear in the code for installing a single(s) receptacle on a branch ckt. Do the same rules apply like in 210.21 B 3 that if there are more than one receptacle on a 20 amp ckt you can have 15 amp receptacle or 20 a receptacle on that ckt. So in this case a single or multiple single 15 amp receptacles on a a 20 amp circuit as long as there are 2 devices on that ckt is fine?
Yes, that's correct. You can have two or more single 15A receptacles on a 20A branch circuit, or one single 15A receptacle along with other outlets on a 20A branch circuit. But you cannot have only one 15A single receptacle as the only outlet on a 20A branch circuit.
Also, is a single receptacle really only designed for a dedicated ckt like a fridge or microwave or is it acceptable on a branch ckt where you want to limit any other loads from being plugged in?
You can put single receptacles anywhere you want.
 
The only thing that doesn’t make sense is that a 15 amp duplex is rated for 20 amps pass through, I don’t know that a single receptacle is rated Although a single 20 amp receptacle can accept a 15 or 20 amp plug.
Yes, that's correct. You can have two or more single 15A receptacles on a 20A branch circuit, or one single 15A receptacle along with other outlets on a 20A branch circuit. But you cannot have only one 15A single receptacle as the only outlet on a 20A branch circuit.

You can put single receptacles anywhere you want.
I feel like it’s just a much more confusing way of saying unless it’s a ckt serving one receptacle for one load then you can have a multiple 15 amp duplex receptacles or multiple single 15 amp
receptacles or a mix of both on a 20 amp circuit. Am I right? Or maybe I’m over analyzing the code again lol
 
You seem to have it correct. Table 210.21(B)(3) summarizes it also.
 
Ok, not to beat a dead horse but everyone agrees that the code saying two or more receptacles they basically mean either a duplex or two singles basically any type of friggin’ receptacle?

Whether it be 10 single receptacles or 5 duplexes all of which being 15 amp on 20 a ckt..

My theory in this is that even a single 15 amp receptacle is the same guts as a 20 amp duplex and that if you only plug a load of not more than 12 amps in that receptacle will not over heat and trip the ckt.

This concludes my concern on this matter. Any input has been appreciated
 
Not sure how it effects your thoughts, but note the 12 amp load limitation {210.21(B)(2)} only apples to a circuit suppliying two or more receptacles or outlets. The Code has no problems with you having a 15 amp load ona 15 amp SINGLE receptacle or 20 amp load on a 20 amp SINGLE receptacle.
 
Not sure how it effects your thoughts, but note the 12 amp load limitation {210.21(B)(2)} only apples to a circuit suppliying two or more receptacles or outlets. The Code has no problems with you having a 15 amp load ona 15 amp SINGLE receptacle or 20 amp load on a 20 amp SINGLE receptacle.
Yes for a dedicated circuit, you can load the ckt to 100% if it’s non continuous. Branch circuits, cord and plug appliances shouldn’t have a rating of more than 80% for that particular device.
 