hitehm
- Las Vegas NV
We had to make room in our main panel that was full, so we installed a small 6 space Eaton sub next to the main connected through a short 8" section of EMT. The feeders plus the 5 returning branch circuits all went through the same 8" of EMT. Then of course the NEC 300.3.B rule came up and we had to make a decision on also splicing over the neutrals and EGCs or keeping them landed in the main panel. In the end we decided to follow the letter of the law and spliced every Hot, N and G from all 5 circuits to the sub. After we we're done I concluded it would've been better to keep the N and Gs landed in the main since it really stressed the wiring to fully relocate these circuits. I won't bore you with the details but it was very tight and very difficult on the wiring to do this.
I have seen several opposing viewpoints on this topic including on this forum. It seems split between those who move everything because of concern for EMI heating effect and staying strictly compliant to 300.3B and those who feel it's best to keep the neutrals and grounds in the main. So my questions are:
1 - Why are the EGCs also required to be brought over as well? This really seemed unnecessary from an electrical stand point since they aren't normally current carrying and also in our case no matter how gentle we were trying to be, put stress on the cables trying to trace them down and untangle them from each other.
2 - For practical purposes, is there a minimum distance that's considered a "raceway" when deciding to be strict to 300.3B? We didn't use a nipple because of the angle but there was only 8" between main and sub.
3 - What if we used PVC between main and sub? No EMI can induce in the conduit causing heat so why isn't there an exception for all nonmetallic conduit?
4 - What is anyone's opinion about how literal you need to be with 300.3B, especially when just relocating to a very close sub panel and what do you normally do in this situation?