Zyb Member Location Maine Occupation Design Engineer Aug 11, 2022 #1 Hi, Utility is asking for combined fault current for the PV System. anyone knows how to compute this?
G ggunn PE (Electrical), NABCEP certified Location Austin, TX, USA Occupation Consulting Electrical Engineer - Photovoltaic Systems Aug 11, 2022 #2 Zyb said: Hi, Utility is asking for combined fault current for the PV System. anyone knows how to compute this? Click to expand... SMA has a published tech paper for their inverters: https://files.sma.de/downloads/Iscpv-TI-en-20.pdf
P pv_n00b Senior Member Location CA, USA Occupation Professional Electrical Engineer Aug 12, 2022 #3 If you can't get it for the inverter you are using it's generally acceptable to estimate the SC current to be 1.2-1.5 times the FLA of the inverter.