Over the last few years, we have been doing T-Mobile and Verizon small cells on utility poles and street lights. The utility standards put out for work on the power company poles are the guidelines we must follow. One thing is to use the pole ground as the GEC. We use a copper C and crimp the wire that runs from utility neutral to the one rod at the base. The city electrical inspector would not sign off without the two ground rods so we installed an additional one. The standards called for SCH 40 PVC conduits from the ground up on the opposite side of the pole from traffic. The inspector called out exposed to physical damage. The car would have to go thru the utility pole to get damaged Schedule 80 or not, regardless we changed it. I don't think the utility will care about the SCH 80. The third item was additional support on the pole. The utility standard requires the standoff on the poles to be 8' above finished grade this is to keep someone from walking into the end and getting hurt. NEC requires support at 5' so we added a standoff bracket below 5' from the ground. I believe the utility is going to reject the site or just remove the bracket. I had this case once before out of probable about 100 sites. The services are 15' in the air this one went down to go up a different pole across the street. Most go up to an aerial strike. Even in the air above 15' the utility freaks out if we place a standoff every 5' on their poles but certain inspectors only care about the NEC standard regardless of it being on the utility pole. Utilities are excluded from the NEC. Thoughts about a lease agreement on the poles and NEC jurisdiction? The plans from the utility are stamped engineered documents. At this point, we just do what the inspector asks and pass it off, and then do what the utility says to appease them. I feel that the NEC should only apply to the electrical service enclosure that it installed safely and correctly per the NEC with the Neutral bonded to the GEC, labeled, AIC and arc flash, etc. The utility pole and conduits are part of the utility.