main197
Member
- Location
- California
- Occupation
- EE
Assuming the tap in the primary is at the normal position. Can a defect in the transformer cause this?
I do not have all the information yet, but I was told the Powerlogic meter shows primary voltage between 12kV- 12.1 kV. And the secondary reading is around 460V.Absolutely.
Partially Shorted windings
So how do you know the primary matches the data plate?
Example. How do you know there isn’t 11,485 volts on the primary?
Go into the Powerlogic meter setup and see what the PT information is.I do not have all the information yet, but I was told the Powerlogic meter shows primary voltage between 12kV- 12.1 kV. And the secondary reading is around 460V.