I’m told by several generator installers that when installing a Generac 200a 1P ATS off a single 200a meter combo on a single family dwelling that you can’t just install your feeder wires, 2 hots and 1 neutral, off the load side of the first means of disconnect and land them to the utility side of the ATS and bonded neutral bus and only run the 2 hot feeders back to the meter combo tapping the feeders that go to the panel.
They say I must run a neutral from the ATS back to the meter combo where I’m tapping the original feeders.
I can’t find any code that supports this. I’ve never been failed by an inspector for doing this. Any code help?
They say I must run a neutral from the ATS back to the meter combo where I’m tapping the original feeders.
I can’t find any code that supports this. I’ve never been failed by an inspector for doing this. Any code help?