ramsy
NoFixNoPay Electric
- LA basin, CA
- Service Electrician 2020 NEC
Exact same wording in 2017 NEC 620.85 (last sentance) for "sump pumps" in elevator shafts.Here in NJ GFCI protection is not required for a single receptacle serving a sump pump.
Have dealt with Zoeller sump pumps. Most instructions exclude direct hard-wire without GFCI.From the Wayne Installation manual. "FOR ADDED SAFETY the receptacle must be protected with a ground fault circuit interrupter (GFCI)."
Read more: https://manuals.plus/wayne/submersible-sump-pump-system-manual#ixzz7aWaSirz2
My boss told me to always follow the code. and the instruction manual.
If you ever have to go on a witness stand and answer questions. you're going to have a lot easier time of it.
"2. Make certain that the ground fault interrupter protected receptacle or control box is within the reach of the pump’s power supply cord. DO NOT USE AN EXTENSION CORD."
Except for Zoeller models 429x Agricultural, & 900 Prepackaged systems, which don't require separate GFCI-protected feeders.