Construction
Southwire Armorlite® Type MC Cable is constructed with soft-drawn copper, Type THHN/THWN conductors rated 90°C dry available in sizes 14 AWG through 2 AWG, and a green insulated grounding conductor. The conductors are cabled together and a binder tape bearing the print legend is wrapped around the assembly. Aluminum interlocking armor is applied over the assembly.
It's ironic that the one cable type they specify a particular insulation rating for can never be used at that rating.Unlike NM cable which is required by the NEC to have conductors rated for 90° C as Don stated MC cable does not have that requirement. I think that for sake of argument you could say that all modern MC cable is constructed with 90° C conductors.