The POCO refers to "320A self contained meter socket " is a 400 breaker set to trip at 320A.

My question is, are all main breakers set to trip at 80% ?

Will a 200A trip at 160?

The question is specific to 120/240 residential single phase.

Are mains supposed to be sized at 80% load for residential?
 
Not sure what your poco is referring to?
Breakers trip at their rating, not 80%, bu note the trip point is based on a time current curve, a 200 amp breaker will never trip at 200 amps
 
Sent some breakers rated at continuous use 3 hours or more at full current rating? while others are not, thus 80%?
 
phone changed my wording “Sent” = isn’t some breakers rated at continuous?
 
The trip curve for 80% and 100% continuous rated breakers is the same. What the actual difference is (or was, if this is a vestigial code thing) is a mystery.
 
The trip curve for 80% and 100% continuous rated breakers is the same. What the actual difference is (or was, if this is a vestigial code thing) is a mystery.
My understanding is that every breaker passes a test at 100% current in free air (unenclosed). Whereas a 100% rated breaker passes a 100% current test in a specified enclosure, which you need to use in your installation to achieve the 100% rating.

Cheers, Wayne
 
The trip curve for 80% and 100% continuous rated breakers is the same. What the actual difference is (or was, if this is a vestigial code thing) is a mystery.
It is all about heat disappation.
Every breaker is UL tested at 100% in open air.
Breakers are applied at 80% when they are mounted into enclosures.
Breakers in properly ventilated enclosures maybe applied at 100%.
 
Not sure what your poco is referring to?
Breakers trip at their rating, not 80%, bu note the trip point is based on a time current curve, a 200 amp breaker will never trip at 200 amps
When you say it will never trip at 200A what do you mean? Could you explain plain a little more in depth. Thank you in advance
 
It is all about heat disappation.
Every breaker is UL tested at 100% in open air.
Breakers are applied at 80% when they are mounted into enclosures.
Breakers in properly ventilated enclosures maybe applied at 100%.
So is a fair assumption that your average breaker in an enclosure will trip at 80% load if it is under 80% load for 3hrs or more
 
The trip curve for 80% and 100% continuous rated breakers is the same. What the actual difference is (or was, if this is a vestigial code thing) is a mystery.
Would you mind explaining more about the trip curve as it applies to 80% and 100%. I don't understand
 
So is a fair assumption that your average breaker in an enclosure will trip at 80% load if it is under 80% load for 3hrs or more
No.
You need to consider the breaker trip curve as well as it's ambient temperature. For example a UL489 listed breaker can carry up to 130% of its current rating for periods in excess of 1 hour at 40C.

But remember breaker and fuse performance and conductor ampacity are all compatible when applied per the NEC.
 
Do breakers have different trip curves based on brand or type? Where can I find more info on trip curves? Would you happen to know?
All major overcurrent protective device manufacturers have publications on these curves.
 
All major overcurrent protective device manufacturers have publications on these curves.
Last question Jim, I really appreciate your responses. I am reading up on it and I don't understand why a couple people have said: The trip curve for 80% and 100% continuous rated breakers is the same.
 
Last question Jim, I really appreciate your responses. I am reading up on it and I don't understand why a couple people have said: The trip curve for 80% and 100% continuous rated breakers is the same.
Because it is.
The 80% factor is simply a SWAG used to adjust for an open air device rating being mounted internal to an enclosure.

All UL conductors and overcurrent protective devices are evaluated at 100%. The 80% debating basically provides a margin of error for the actual installation condition being different than those in the testing labs.
 