Electromatic
- Virginia
- Master Electrician
I was recently trying to explain dwelling service sizing to some coworkers and of course came out confusing myself. I was thinking through meter-mains with branch breakers, 400A services with 2 panels, etc. Now I'm wondering what the actual "service rating" is when it says, "...conductors...ampacity not less than 83 percent of the service rating." The handbook says the 83% is based on the "...disconnect rating. The calculation is not based on the overcurrent device protecting the main feeder."
Say I had a calculated load of 210A. 210 * .83 = 174.3A If I use 4/0Al with 180A ampacity, I'm good for the load and the re-inserted Table 310.12 and can next-size-up to a 200A breaker/disconnect. What if I choose 2/0Cu? It's good for 175A. The table says it's good for a 200A service, but 175A is a standard OCPD size.
I think I read another forum member saying to choose an OCPD size then take 83% of that to size your conductors. That seems contrary to how you approach most other calculations.
I might just be thinking about it too much!