For me table 220.55 has always been the hardest to grasp in article 220
There is an oven rated 2200kw
and a cook top rated 11500kw
What is the demand load? I am getting 11kw is this correct?
If I recall you can add the watts of one oven and one cooktop and use column C and treat it as one range.
That would mean 1 unit at 14kw but I believe you can also do them separately using col A and C
Average the two using 12 as the smallest number...gives you an average of 17.... 5% for each kw over 12... If I did the math correct = 14
Look at Example D6B in Annex D (Pg 799 in '17)
I still don't get it. Note #4... This is for branch circuit but I assume it would be the same for the demand load
The example you showed was for ranges only. You are dealing with averages here we are not just using Note #4
If someone thinks note #4 doesn't apply for demand load then you would have to use each one individually. The 11.5 kw = 12 kw = 8kw demand from table
2.2 kw *80% = 1.76 =
8kw + 1.76 Kw = 9.76= 10 kw
I'm confused now, is the answer 8800W or 10000W lol
IMO... it 8.8
If this is for a test I believe 8.8 is the answer. The 10kw is another way to calculate it. Using Note 4 I see the answer as 8.8
If you have 2 units- cooktop and oven they can be added together. Let's face it a range is nothing but a cooktop and an oven. I would just ignore the 10kw it complicates things and wasn't necessary.