The service (Electrical Panel 120/240 volt High Leg) available on-site is an open-delta configuration which only utilizes 2 transformers and provides a 3-phase service (L1 to L2=240V, L2 to L3=240V, L1 to L3=240V, and L1 to Ground=120V, L2 to Ground=208V, L3 to Ground=120V). The FRONIUS -Symo advance (12.0-3, 208-240) has a provision for a High Leg grid connection.
But now the Utility company is saying - The inverter that was selected is a 3-phase 240V connection, but the service transformer is an open delta (2 phase). A 3-phase inverter is not allowed to be on an open-delta transformer. If you choose to install a 3-phase inverter, the open delta bank will need to be closed, and the report will include the cost to upgrade it to a 3-phase closed delta bank with the 3rd transformer can being large enough to support this application. If you choose to install a single-phase inverter, the existing transformer can will need to be upgraded to support this application unless this application is downsized enough to avoid the upgrade.