So I was reading over this forum thread: https://forums.mikeholt.com/threads/transformer-voltage-drop.101920/
It basically talks about an inspector requiring someone to do a voltage drop calculation and to include the voltage drop across the stepdown transformer.
My question is when doing a voltage drop calculation where you have, lets say, a 480V bus distribution system, and then a 480-208/120V step down transformer and you are doing the calculations by hand, do you include some sort of voltage drop across the transformer?
From the thread above it was nicely explained that the secondary voltage is going to be less than the nominal due to "voltage regulation" (if you have a leading PF it can actually even be higher) but as far as VD calculations, how does this get captured? By using SKM it shows the VD before the transformer and the VD on the bus after and it is very significant. For my particular transformer/case it goes from 1.4% or so to 3.8% VD by looking at the bus before the transformer and the bus immediately after.