SuburbanSparks
- chicago, il
- Electrical Contractor
Hi All,
I wanted your opinion on this amendment and how you read this. They way I read it is in the exceptions #1 and 2 that arc faults are not required if its in conduit and its an extension of the circuit, primarily for remodeling work. The inspector argues its for Dorms. But it reads to me at least that dwelling units, i.e a house or a 2 flat, 3 flat etc... would also count.
Here's the amendment.
Article 210.12 Arc-Fault Circuit-Interrupter Protection. (Revised to read as follows)
Arc- fault circuit-interrupter protection shall be provided as required in 210.12(A), (B), (C) and (D). The arc-fault circuit interrupter shall be installed in a readily accessible location.
(A)
Dwelling Units. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets and devices installed in dwelling units shall be protected by a listed arc-fault circuit interrupter, combination-type, installed to provide protection of the branch circuit.
(B)
Dormitory Units. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets and devices installed in dormitory units shall be protected as described in 210.12(A).
(C)
Guest Rooms, Guest Suites and Patient Sleeping Rooms in Nursing Homes and Limited-Care Facilities. All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets and devices installed in guest suites, guest rooms of hotels and motels and patient sleeping rooms in nursing homes and limited-care facilities shall be protected as described in 210.12(A).
(D)
Branch Circuit Extensions or Modifications - Dwelling Units, Dormitory Units, and Guest Rooms and Guest Suites. In any of the areas specified in 210.12(A), (B) or (C), where branch- circuit wiring is modified, replaced or extended, the branch-circuit shall be protected by one of the following:
(1)
A listed combination-type AFCI located at the origin or the branch circuit.
(2)
A listed outlet branch-circuit type AFCI located at the first outlet of the existing branch circuit.
Exception No. 1 to 210.12(A), (B), and (C): It shall be permitted to omit AFCI protection for that portion of the branch circuit enclosed in rigid metal conduit (RMC), flexible metal conduit (FMC), intermediate metal conduit (IMC), electrical metal tubing (EMT), or Type MI cable sheath meeting the requirements of 250.118 along with metal outlet and junction boxes.
Exception No. 2 to 210.12(D): It shall be permitted to omit AFCI protection for that portion of the branch circuit installed in rigid metal conduit (RMC), flexible metal conduit (FMC), intermediate metal conduit (IMC), electrical metal tubing (EMT), or steel sheathed cable, Type AC, Type MC, or Type MI cable sheath, meeting the requirements of 250.118, with metal outlet and junction boxes.
Exception No. 3 to 210.12(A), (B), (C) and (D): Where an individual branch circuit to a fire alarm system is installed in accordance with 760.41(B) or 760.121(B) is installed in rigid metal conduit (RMC), intermediate metal conduit (IMC), electrical metal tubing (EMT), or Type MI Cable sheath meeting the requirements of 250.118, with metal outlet and junction boxes, AFCI protection shall be permitted to be omitted.
(A)
(B)
(C)
(D)
(1)
(2)