Is there a best practice for what the max length should be when using 4/0 SER Aluminum from the Service Disconnect to the interior main panel? I have a service disconnect that is about 75 feet from the main panel. Wondering if 250 kcmil should be used instead.
 
Is there a best practice for what the max length should be when using 4/0 SER Aluminum from the Service Disconnect to the interior main panel? I have a service disconnect that is about 75 feet from the main panel. Wondering if 250 kcmil should be used instead.
I'll bet pretty much everyone would use 4/0 for that.
 