680.40 General. Electrical installations at spas and hot tubs
shall comply with the provisions of Part I and Part IV of this
article.
Where in article 680.41 2011 nec does it give the location of disconnect . for hot tub one family dwelling?
In Sight From (Within Sight From, Within Sight). Where this
Code specifies that one equipment shall be “in sight from,”
“within sight from,” or “within sight of,” and so forth, another
equipment, the specified equipment is to be visible and not
more than 15 m (50 ft) distant from the other.
680.12 Maintenance Disconnecting Means. One or more means to simultaneously disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be readily accessible and within sight from its equipment and shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool, spa, or hot tub unless separated from the open water by a permanently installed barrier that provides a 1.5 m (5 ft) reach path or greater. This horizontal distance is to be measured from the water’s edge along the shortest path required to reach the disconnect.
thank you !!!!!!!!!!!!!!This is for the maintenance disconnect and we also know it cannot be more than 50'. Motor disconnects must be in sight from