nizak

Senior Member
I have an install where 2 circulation pumps that are part of a geothermal system are located remotely from the heat pump. Both pumps get their power from a relay located in the unit. Would the disconnecting means for the heat pump meet the requirement for the circulation pumps even though it's on the main level and the pumps are in the crawl space?
Thanks
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Then you need a disconnect within sight.

There are exceptions, mostly having to do with industrial installations under engineering supervision with established safety protocols, but that never applies to a residential installation.
 