Entrance through wall

Status
Not open for further replies.

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
what else is required between an outside wall and double gang box outside listed specifically to run romex NM cable10-2 through a wall hole and hole through box. Sealant around box, extra sleeve? 1/4 inch romex sleeve out of box (not pictured)

Main concern is requirement between holes of wall and box
 

Attachments

  • 09628136-8CCB-4A13-8553-09A2A6538BC5.jpeg
    09628136-8CCB-4A13-8553-09A2A6538BC5.jpeg
    29.3 KB · Views: 49
  • ADA38A14-3FE2-4032-8232-013DA0E24576.jpeg
    ADA38A14-3FE2-4032-8232-013DA0E24576.jpeg
    25.3 KB · Views: 47
That is not NM cable. the run should be in conduit.
 
That is not NM cable. the run should be in conduit.
Agreed and if it was/is NM the jacket is not present. In any case it would need a proper connector so the entrance hole is not correct.

With that said the OP needs to consult with his supervisor for help.
 