Little Bill Moderator Staff member Location Tennessee NEC:2017 Occupation Semi-Retired Electrician Sep 28, 2022 #1 Is 240.24 for any breakers/fuse in a panel, or just the main breaker/fuse? Better put, is the height just for the main or for a branch circuit should the panel be upside down?
Is 240.24 for any breakers/fuse in a panel, or just the main breaker/fuse? Better put, is the height just for the main or for a branch circuit should the panel be upside down?
A AC\DC Senior Member Location Florence,Oregon,Lane Occupation EC Sep 28, 2022 #2 Any breaker main or branch.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Sep 28, 2022 #3 I always wondered why we need 404.8 in the NEC when we already have 240.24?
J jaggedben Senior Member Location Northern California Occupation Solar and Energy Storage Installer Sep 28, 2022 #4 infinity said: I always wondered why we need 404.8 in the NEC when we already have 240.24? Click to expand... 404.8 applies to unfused switches, 240.24 doesn't. I wasn't aware of 240.24 and was wondering the opposite from yiu
infinity said: I always wondered why we need 404.8 in the NEC when we already have 240.24? Click to expand... 404.8 applies to unfused switches, 240.24 doesn't. I wasn't aware of 240.24 and was wondering the opposite from yiu