How would I determine what a normal voltage drop would be when a washing machine agitates? I was measuring voltage at the receptacle and it was dropping 4 volts everytime it agitated.
I wouldn't worry about it.How would I determine what a normal voltage drop would be when a washing machine agitates? I was measuring voltage at the receptacle and it was dropping 4 volts everytime it agitated.
Thats slightly over 5%. I agree it's not too concerning.I wouldn't worry about it.
Normally not so much an issue unless it is creating a drop that is affecting other equipment or lighting. Neither of which was mentioned by OP. But there are several threads that ask about light flicker or other effects when washer running.Thats slightly over 5%. I agree it's not too concerning.
A bigger issue would be if the voltage is going up on the other hot at the time it drops at the washer.How would I determine what a normal voltage drop would be when a washing machine agitates? I was measuring voltage at the receptacle and it was dropping 4 volts everytime it agitated.
A bigger issue would be if the voltage is going up on the other hot at the time it drops at the washer.
What is the voltage change at the service as the washer
If I thought the voltage drop was to high I would want to know how much of a load I was adding to the circuit. Use your ammeter to see the change in load. Then come up with some sort of the length for the cable ( probably a bit of an estimation). Then do a voltage drop calculation.How would I determine what a normal voltage drop would be when a washing machine agitates? I was measuring voltage at the receptacle and it was dropping 4 volts everytime it agitated.
That's a darn good question.Why were you testing the vd in the first place?
For me it would have been because I have a new meter.That's a darn good question.
Why were you testing the vd in the first place?
I noticed the UPS that I have on my main office computer would flag an occurrence when the laser printer cycled. I did as you have suggested and the calculated was very close to the measured.If I thought the voltage drop was to high I would want to know how much of a load I was adding to the circuit. Use your ammeter to see the change in load. Then come up with some sort of the length for the cable ( probably a bit of an estimation). Then do a voltage drop calculation.
I was testing voltage at the receptacle and the washing machine happened to be plugged in runningWhy were you testing the vd in the first place?
Just sparked my curiosity reallyI was testing voltage at the receptacle and the washing machine happened to be plugged in running
How far is the wire run is my next immediate question. In some of the houses it's not hard to run over a 100 feet from a source panel to an appliance. A good designer knows to put things closer but not always.
Thats slightly over 5%. I agree it's not too concerning.