www.afcweb.com
If the lighting is in a patient care area, the wiring method must comply with 517.13(A).I have yet to ask any vendors that our company buys from so I don't have any input other that a question. In health care facilities are the lighting circuits required to use HCF MC?
Does 517.13(B)(1)(4) exception 2 give you any relief from the raceway qualifying as a equipment grounding conductor plus having a full size equipment grounding conductor for luminaires located above 7-1/2’ in patient care areas.If the lighting is in a patient care area, the wiring method must comply with 517.13(A).
You are correct MC is not a raceway! I have not seen the difference in price for a long time between hcf and mc. However if you are doing a lot of wiring in Patient care areas and also in non patient care areas the difference in price might be well worth having two different types of cable!Yes. Luminaires located above 7-1/2’ in patient care areas and switches outside the patient care areas can be treated as outside the patient care area and wired using non-HCF cable. But as @augie47 said, why bother with two wiring methods.
I notice you refer to raceway. MC cable is not raceway.
-Hal