main197
- California
- EE
Thanks. How about 312.6 (B)? Does it apply here?As far as deflection of conductors at the breaker. In this case 312.6(A), 6"
Thanks. Does 312.6 (B) apply here?There is are bending radius rules in the NEC for single conductors 1000 volts or less.
There is a rule to provide bending space in 312.6(A), but that does not have anything to do with the actual radius you can bend on the conductor.
If I ever get a moment to look it up I will.There is a rule to provide bending space in 312.6(A), but that does not have anything to do with the actual radius you can bend on the conductor.
Correction: The red text is corrected text from my original post.
I cheated and googled it .. maybe this is correct.If I ever get a moment to look it up I will.
You do realize that section is for conductors above 1000v don't you?I cheated and googled it .. maybe this is correct.
as posted ..
300.34 Conductor Bending Radius
The conductor shall not be bent to a radius less than 8 times the overall diameter for nonshielded conductors or 12 times the overall diameter for shielded
Yes a common mistake when applying a non-existent bending radius restriction to 600 volt conductors.You do realize that section is for conductors above 1000v don't you?
I suppose the point that there is a radius limit to a variety of conductors is apparent were some suggest there is no such rule.You do realize that section is for conductors above 1000v don't you?
All of the cable articles have a minimum bending radius in the NEC...there just is not any minimum bending radius for a single conductor rated 1000 volts or less.I suppose the point that there is a radius limit to a variety of conductors is apparent were some suggest there is no such rule.
Here's another one 320.24
According to NEC Article 320.24, for AC cable, the radius of the curve of the inner edge of any bend shall not be less than 5 times the diameter of the cable.