Main breaker for Milbank combo panel.

Status
Not open for further replies.
Why not? Sounds like a MLO panel and he wants to install a 200A branch. As long as there is no specific restriction listed on the thing whats the problem? Its probably a Siemens Q2200B
It would have to be reconfigured differently from how it is put together at the factory 🤷‍♂️

It comes with 1+3 bridged and 5+7 bridged

It would need 1+5 and 3+7

Maybe use short pieces of #2 copper, effectively paralleling out from breaker to some Polaris taps to get back to single conductors to feed new panel.
Screenshot_20221022_220256_Chrome.jpgScreenshot_20221022_220139_Chrome.jpg
 
It would have to be reconfigured differently from how it is put together at the factory 🤷‍♂️

It comes with 1+3 bridged and 5+7 bridged

It would need 1+5 and 3+7

Maybe use short pieces of #2 copper, effectively paralleling out from breaker to some Polaris taps to get back to single conductors to feed new panel.
View attachment 2562617View attachment 2562618
No you have the wrong breaker. The correct one (pretty sure I had the right part number) is a branch breaker. The one you showed is a replacement for a factory 200A main breaker.
 