I am having an issue at my residence where there is significant harmonic distortion and I believe the cause of my UPS constantly alternating between battery and line power. The issue has occurred ever since we moved into our house back in March although has been progressively worse the past month and a half. Through monitoring of both the UPS and a Fluke 179 I noted voltage and frequency were all within spec and could not determine any anomalies. My utility company even put in a recorder to monitor at the meter and did not see any anomalies over a 3-4 week period either (as far as I can tell it was just measuring voltage and load).
I then came across harmonics and began to dig into that. I went around my house and at the outlet (dedicated 20A circuit that was recently run) to the UPS I measured THDv% between 9.1-11.4%. I went downstairs to my breaker panel, turned off the master switch, and still measured 11.1% prior to the switch:
The third harmonic seems to have the significant amount of distortion when I go through the first 25 harmonics. This morning, I measured and at THDv 9.8% I have the following:
h01 - 100%
h02 - 0.0%
h03 - 9.7%
h04 - 0.0%
h05 - 1.8%
h06 - 0.0%
h07 - 0.4%
h08-25 - 0.0%
As far as the UPS is concerned, I've taken it and run it for 15 minutes at a couple neighborhood homes (within a 3 mile radius as the crow flies) and a couple commercial buildings. The two other neighborhood homes that, like mine, have a single phase feed also exhibited issues. Similarly, when I measured THDv at one of them it was also in the 9s. The Starbucks down the road the UPS was on line power the entire time and THDv there was 2.6%. That is fed by a three phase padmount transformer.
1. Are there any further data points or tests I can do to narrow down what the issue is?
2. Any tips of getting someone from my utility that has knowledge of harmonics to assist in investigating?
3. If unsuccessful at getting to the root cause, is there any way to mitigate the high THDv% I'm seeing (eg filter etc), that is realistic from a practical and cost perspective for residential?
Thank You!
h01 - 100%
h02 - 0.0%
h03 - 9.7%
h04 - 0.0%
h05 - 1.8%
h06 - 0.0%
h07 - 0.4%
h08-25 - 0.0%
Thank You!