A question In my book for licensing prep ask:
Determine the MINIMUM size THHN copper conductors required to supply a 3 hp, 240 volt, single phase continuous duty motor when terminations have a rating of 75 degrees Celsius.
Book says answer is (B) 12 AWG
Motor FLC = 17 amperes
17i x 1.25% table 430.22 = 21.25 amperes
(I’m good at this point)
But then study book says, Size 12 AWG THHN is rated at 25 amperes at 75 degree Celsius (Table 310.15 (B)16)
NO IT IS NOT!!!
Nec table 310.16 for not more than 3 current carrying conductors in a raceway shows 12 AWG wire at 75 degree Celsius good for 25 amperes
and 14 AWG!!! THHN wire rated 90 degrees Celsius For 25 AMPERES!! But not 12 AWG THHN as study book suggest
Therefore we should be selecting 14 AWG THHN rated 90 degrees if using THHN at higher temp rating and book is WRONG???
I’m still not getting temperature terminations apparently?
Determine the MINIMUM size THHN copper conductors required to supply a 3 hp, 240 volt, single phase continuous duty motor when terminations have a rating of 75 degrees Celsius.
Book says answer is (B) 12 AWG
Motor FLC = 17 amperes
17i x 1.25% table 430.22 = 21.25 amperes
(I’m good at this point)
But then study book says, Size 12 AWG THHN is rated at 25 amperes at 75 degree Celsius (Table 310.15 (B)16)
NO IT IS NOT!!!
Nec table 310.16 for not more than 3 current carrying conductors in a raceway shows 12 AWG wire at 75 degree Celsius good for 25 amperes
and 14 AWG!!! THHN wire rated 90 degrees Celsius For 25 AMPERES!! But not 12 AWG THHN as study book suggest
Therefore we should be selecting 14 AWG THHN rated 90 degrees if using THHN at higher temp rating and book is WRONG???
I’m still not getting temperature terminations apparently?