Voltage is fine on line sideIs there a corresponding voltage imbalance on the input side?
Since the line-to-line voltage peaks directly drive the DC bus through a bridge rectifier, the current drawn will be higher for higher voltages.
Had this problem maybe 10 years ago and it was from a defective IGBT. We had over 500 VFD'S that we PM'ed from once to four times a year. Never had a rectifier or rectifier bridge go bad. When I had such a large difference in output ampere I would place the drive in hand and start at 10% and take both ampere & voltage readings using the LCB ( What Danfoss calls Local Control Panel ) = touch screen then raise it 10% more and keep taking readings until It reached full speed ( 100 % ). ( First few times gave tech support guys this info )Danfoss & Allen Bradley had great tech support and ABB the worst. Would call them a few times a year and they are great at locating problems. I kept troubleshooting problems & fixes in a copy book to help in troubleshooting. Appears with drives probably 85% of the problems where from same maybe 5 reoccurring problems: Bad IGBT, if tripping out at full speed but not at 90 to 94% full speed problem with load such as large air handlers lovers only partially open, runs on hand but not automatic often a control issue, if you have bypass with two or most times three contactors the M2 ( OUTPUT contactor ) goes bad at least twenty times more then the M1 input contactor, Had 12 & 15 year old drives in a secured area that parameters would change on their own and some times people change parameters without telling or recording it. Had people change maximum speed output lower. As far as the DC BUSS issue if the line voltage is 480 volts then the DC Buss should be from 650 to 675 volts DC. Old drives had terminals where you could take measurements but in at least last 20 years you can read DC Buss from the touch screen. If the DC is low and all three input lines at or close to 480 volts and DC Buss low then it's a rectifier problem. Some drives use three separate rectifiers but majority use a one piece three phase input rectifier. 3 line wires in & two DC wires out. From one to 6 or more capacitors are wired across the DC Buss.They are rated for 75,000 hours but had several old drives with over 125,000 hours run time with original capacitors. Did you try bypassing the drive & running motor and taking amp readings ? If it runs across the line this would eliminate one of the six motor windings ( if dual voltage ) being source of problem.Is there a corresponding voltage imbalance on the input side?
His current discrepancy is on one of the input leads. About has to be a rectifier problem in that particular input, or any other circuit component up to where that current enters the DC bus.Had this problem maybe 10 years ago and it was from a defective IGBT. We had over 500 VFD'S that we PM'ed from once to four times a year. Never had a rectifier or rectifier bridge go bad. When I had such a large difference in output ampere I would place the drive in hand and start at 10% and take both ampere & voltage readings using the LCB ( What Danfoss calls Local Control Panel ) = touch screen then raise it 10% more and keep taking readings until It reached full speed ( 100 % ). ( First few times gave tech support guys this info )Danfoss & Allen Bradley had great tech support and ABB the worst. Would call them a few times a year and they are great at locating problems. I kept troubleshooting problems & fixes in a copy book to help in troubleshooting. Appears with drives probably 85% of the problems where from same maybe 5 reoccurring problems: Bad IGBT, if tripping out at full speed but not at 90 to 94% full speed problem with load such as large air handlers lovers only partially open, runs on hand but not automatic often a control issue, if you have bypass with two or most times three contactors the M2 ( OUTPUT contactor ) goes bad at least twenty times more then the M1 input contactor, Had 12 & 15 year old drives in a secured area that parameters would change on their own and some times people change parameters without telling or recording it. Had people change maximum speed output lower. As far as the DC BUSS issue if the line voltage is 480 volts then the DC Buss should be from 650 to 675 volts DC. Old drives had terminals where you could take measurements but in at least last 20 years you can read DC Buss from the touch screen. If the DC is low and all three input lines at or close to 480 volts and DC Buss low then it's a rectifier problem. Some drives use three separate rectifiers but majority use a one piece three phase input rectifier. 3 line wires in & two DC wires out. From one to 6 or more capacitors are wired across the DC Buss.They are rated for 75,000 hours but had several old drives with over 125,000 hours run time with original capacitors. Did you try bypassing the drive & running motor and taking amp readings ? If it runs across the line this would eliminate one of the six motor windings ( if dual voltage ) being source of problem.
I've used that method multiple times over the years to reduce the imbalance of current on 3 phase motors. (Typically open Delta systems)
When I had a defective IGBT I was keying in on mainly output current imbalance. When I ran a VFD at lower speeds say 20 & 30% the output currents were close to being balance but as I increased speed the current became more & more unbalanced. I replaced a bad IGBT on a 125 HP air handler and it started ok. First I rang out the motor leads & meggered the motor then ran it on bypass for a few minutes. Started drive up at 10 or 15% then increased 5% at a time . When I got up to around 35% had a loud what sounded like an explosion. Secured power and had smoke coming out of drive. Called our great drive tech in. First thing he asked me before replacing IGBT did I replace the little maybe $150 board that controlled the expensive IGBT. He told me in some models they have a board just to control firing ( believe up to 5,000 times a second )IGBT'S. I would call the tech support and ask if control board could cause such a problem. On a normal drive set up I found that the output frequency increases at the same rate of output frequency. Good way of checking is in a 480 volt drive when the output voltage reaches say 240 volts output frequency should be at 30 Hertz. Years ago I went to an Allen Bradley & a Fincorr drive and never found any company that supplies a detailed troubleshooting Manuel. We had a small hand held A&B troubleshooting device that some times throw a curve ball. If power supply fuse blew it would display bad power supply. Please let me know what the problem was. Even though I'm retired 4 years now still trying to learn, keep up with the NEC and giving any assistance to others.garbo,
Are you saying that in your experience an _input_ current imbalance was caused by an _output_ IGBT problem?
Could you explain how this happens further? I could see if perhaps the output frequency was 60Hz, and there was and output failure, then an output imbalance might be reflected back to the input. But I can't see how an _output_ error could cause a consistent and steady input current imbalance.
If you've experienced this sort of issue, I'd like to understand how the failure works.
Thanks
Jon