LAWaterInspector
 - Los Angeles
 - Inspector
Full disclosure - I'm a water inspector not an electrician or electrical inspector.  I have a project where we have several concrete water tanks with electrical junction boxes/pull boxes mounted on the sides.  We have rigid metal conduit that transitions from underground duct banks and is routed to these electrical junction boxes as shown in the image below.  The conduit is not supported within 3 feet of the junction box as required by NEC 344.30 and it has been identified as a deficiency by the engineer.  The contractor has indicated the supports are not required because the conduit is supported by the ground where it is directly buried, but I can't find anything in the code to support this position.  We also have this issue throughout the site with conduit bodies and other small fittings where we don't have supports within 3 feet.
Questions:
1. From a code perspective, why are supports required within 3 feet of junction boxes, conduit bodies, etc.?
2. Is there any exception for the application shown below where the conduit transitions from below grade to a termination at the box?
3. What are the implications if we don't enforce the code requirement? Could the installation fail over time?
Thanks in advance for your feedback.
<iframe src="https://watersystemsconsulting-my.sharepoint.com/personal/jpickard_wsc-inc_com/_layouts/15/embed.aspx?UniqueId=5f17fab4-3a67-4881-b1cc-2f33a494ee19" width="640" height="360" frameborder="0" scrolling="no" allowfullscreen title="Conduit at Junction Box.png"></iframe>
			Questions: