xformer
- Dallas, Tx
- Master Electrician
For Calculations 220.50 specifies that motors be calculated in accordance with 430.24. If the motor is 240V, does the additional 25% also apply to the Neutral?
What section is the 25% are you asking about a part of?For Calculations 220.50 specifies that motors be calculated in accordance with 430.24. If the motor is 240V, does the additional 25% also apply to the Neutral?
220.50 >>430.24(1) since you have multiple motors in the service.What section is the 25% are you asking about a part of?
Gotcha.220.50 >>430.24(1) since you have multiple motors in the service.