good afternoon forum,
I work as an electrician for a city. We have services that power our signals and street lighting. It is a split buss panel with the top being fed with a 100amp breaker and the bottom having 4 spot for main breakers. we only install a single pole 30 amp breaker in the lower section to power the intersection controller. The service panel has a name plate that calls the service cabinet a 200amp panel. with the top and bottom breakered per out spec we only have 130 amps. though with the 3 open lower main breaker spaces a greater ampacity could be created.
Does this service need to be fed with 3/0 to facilitate the full 200 amps, or can we re-sticker that the service is only 130amps?
I work as an electrician for a city. We have services that power our signals and street lighting. It is a split buss panel with the top being fed with a 100amp breaker and the bottom having 4 spot for main breakers. we only install a single pole 30 amp breaker in the lower section to power the intersection controller. The service panel has a name plate that calls the service cabinet a 200amp panel. with the top and bottom breakered per out spec we only have 130 amps. though with the 3 open lower main breaker spaces a greater ampacity could be created.
Does this service need to be fed with 3/0 to facilitate the full 200 amps, or can we re-sticker that the service is only 130amps?