Temperature termination for soow
Jpflex
Electrician big leagues
Victorville
Electrician commercial and residential
How would I determine SOOW cord temperature per rated amperes?
I know the #2 AWG SOOW is rated between 80 to 95 amperes before temp correction derating and conductor bundling and our SOOW insulation is rated 90 degrees at these ampacities.
However, as boss wants to use SOOW as a feeder from 100 amp breaker main, according to code I must terminate on what the final breaker is rated for, whether it’s rated 60 degrees or 75 degrees Celsius or 60 degrees when circuit is 100 amperes or less.
This means I must use a larger size conductor to dissipate heat for 60 to 70 degrees.
Although SOOW doesn’t appear to go beyond 95 amperes how would I determine the right size SOOW conductor for a specific ampacity at either a 60 degree or 75 degree rating as I would with standard wire such as THHN per NEC table 310.16? Thanks
It is likely that a lug on a breaker is not rated for the fine stranding of flexible cords.
I think all breakers, in the past 30-40 years, have 75°C rated terminations.
how would I determine...
Table 400.5(A)(1)
But, do you really need 100 amps? If not, can you change the breaker for a smaller one or install a smaller one in separate box at the feed end? Then you can run a smaller (and cheaper) size. Depending on site conditions, you may be better off and spend less $$$ by running some S40 PVC and pulling THHN into it.
Table 400.5(A)(1)
Yea I know but I work at a mine and boss is not an electrician so this was his brainstorming.
Apparently he assured me he had enough ampacity at service 35KVA to add 3 more 100 amp breakers at main panel load center to parallel out using SOOW as underground direct burial feeders (Not legal) to another 3 more sub panels.
A 35KVA Single split phase 240 volt service yields under 146 amperes total. So again he’s it appears he’s BS
That’s what i
Two things-
Do MSHA rules apply?
He can add as many 100 amp breakers as will fit, doesn't mean the main won't trip :LOL:.
The boss ought to leave the electrical stuff to the electrician, but I think we all knew that.
That’s what I was going to ask next lol. Can msha override nec?