32Lateralus
- West Coast
- Electrical
As the title says, doing some additions and POCO says existing transformers need to be upgraded. We are adding some 208V 3ph specific loads so it would be best to change the utility secondary from the existing 240V 3ph delta center-tap high leg, to a 208V 3ph Wye system.
There is an existing Service Entrance listed at 240V 3ph 4W delta. If we change the utility transformers out, do we need to change anything physically about this service entrance? Does it need to be relisted by manufacturer and provided with new labels?
We already confirmed motors etc. downstream nameplates list both 208V and 240V. Any other considerations?
Thank you for the help!