Alwayslearningelec
- NJ
- Estimator
Ok back to my xfrmr temp setup. Engineer called me and was not sure if we are code complaint.
3P 70A 277/480v breaker feeding 45kva xfrm. 45 xfrm feeds (3) 120/208v disconnects. These disconnects feed (3) single phase trailer panels.
The disconnect sizes are 125A and (2) 60A.( BTW do they need to be fused). The transformer is located within 25’ of the disconnects but not within sight of each other.
The engineer is referring me to 450.3(B) and note #2 and not sure how to interpret the following last part of note #2.
the total of all the device ratings shall not exceed the allowed value of a single overcurrent device
Any thoughts? Thanks.
The first part of note #2 does say where secondary overcurrent protection is required. Not sure if required in my case so the note #2 wouldn't apply.