mayanees

Senior Member
Location
Westminster, MD
Occupation
Electrical Engineer and Master Electrician
Below is a snip from a picture of a trip unit on a 2000-amp, 480 Volt, Square D SE type breaker in a gov-owned facility that was constructed in 1999. This is what's known as factory-default settings. The longtime pickup LTPU is set for 1.0, and all the other settings are set to minimum. This gives indication that there was never a Power Study performed (Fault, Coordination and now Arc Flash which wasn't really around in 1999), or at least that the breakers were never adjusted.

If you see these types of settings, I advise letting someone know because reliability can be greatly improved with a coordinated system.

1672946831146.png
 
I am surprised they have not had nuisance tripping of the main.
 
If the engineer who specified that breaker did not specify the desired settings, that's an engineering failure. Either way it's a failure on the part of the installing electrician, who either failed to use the settings given or failed to ask for the settings if they were not given.
 
I am surprised they have not had nuisance tripping of the main.
If they haven't had tripping issues it would appear the coordination is acceptable. This would not be surprising if most of the branch devices are less than 25% of the main device size.
 