Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
If you have metal 4 square boxes made out with neutral to neutral, hot with hot, and then all grounds connected together as typical to feed 120v receptacles downstream.
Which are all connected with 1/2“ emt connected via metal compression connectors to feed downstream receptacles in a metal outlet box and you bond at receptacle box then is it really necessary or code required to redundantly bond every receptacle and or boxes since they are all interconnected via continuous EMT to ground?
Or will code allow only bonding/grounding at receptacle boxes or even just at one receptacle box?
Boss doesn’t want me to use emt instead of ground. And insist I install a ground with each raceway. ( I know it’s redundant again but emt can be used as a ground)
Thanks
Which are all connected with 1/2“ emt connected via metal compression connectors to feed downstream receptacles in a metal outlet box and you bond at receptacle box then is it really necessary or code required to redundantly bond every receptacle and or boxes since they are all interconnected via continuous EMT to ground?
Or will code allow only bonding/grounding at receptacle boxes or even just at one receptacle box?
Boss doesn’t want me to use emt instead of ground. And insist I install a ground with each raceway. ( I know it’s redundant again but emt can be used as a ground)
Thanks