If a motor is fed from a breaker, originating from a main service panel, such as an All-in-One on a residence, is that circuit a Branch for Feeder?
Branch Circuit, Individual.
A branch circuit that supplies only one utilization equipment.
Feeder.
All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.
As long as the motor disco contains OCPD.Thanks guys! I'm understanding that the circuit from the breaker to the motor disco, by definition is a feeder, and the wiring from the disco to the peckerhead is a branch circuit.
Thanks guys! I'm understanding that the circuit from the breaker to the motor disco, by definition is a feeder, and the wiring from the disco to the peckerhead is a branch circuit.
I agree. IMO the fuses in the disconnect are supplementary protection making it a branch circuit.I had a cmp member agree with me but my proposal did not make it. If there is overcurrent protective device in the disconnect then one part is a feeder and the other a branch circuit but if there is no overcurrent protective device then the entire run is a branch circuit... doesn't make sense in this situation
If there is say a reduction in conductor size and similar reduction in overcurrent device then it possibly is a feeder then branch circuit.I agree. IMO the fuses in the disconnect are supplementary protection making it a branch circuit.
Seems to me there's a simple test for when that interpretation is applicable. Namely, if you deleted those fuses, would you still have an NEC-compliant installation, as far as OCPD and conductor sizing? If so, then you can call those fuses supplementary. If not, they are clearly not supplementary.I agree. IMO the fuses in the disconnect are supplementary protection making it a branch circuit.
Excellent way to approach this.Seems to me there's a simple test for when that interpretation is applicable. Namely, if you deleted those fuses, would you still have an NEC-compliant installation, as far as OCPD and conductor sizing? If so, then you can call those fuses supplementary. If not, they are clearly not supplementary.