Mr. Serious
- Oklahoma, USA
- Electrical Contractor
We just today finished installing a feeder to a spa. The feeder goes for about 35 feet along the house and then for about 60 feet out to a 6-space panel with a 50A GFCI breaker for the spa and a 20A circuit for a receptacle. Then about 8 or 9 feet to the spa (more wire than that because it goes down and back up).
It passed inspection, but I was thinking about it after we were done and thought we should have installed two ground rods out at the spa panel because it is separate from the house. Wouldn't it be considered a separate structure in need of its own grounding under the NEC?
Separate question, somewhat related: does a self-contained spa need to be bonded back to the panel serving it with #8 solid copper? I think it actually does not, but it would if it were built into the concrete like a pool, instead of self-contained.
One time I also ran across a site where they wanted a new spa circuit to come off a pre-existing pool panel, but the panel was some distance away from both the house and the required spa disconnect. In this case, would we need ground rods both at the pool panel and at the spa disconnect? The distances involved were house to pool panel about 130 feet, then pool panel to spa about 90 feet back towards the house.