fandi
- Los Angeles
- Electrical Engineer
Hello All,
There’s a mixed use building (Residential + Retails) with a main service switchboard MSB: 4000A Bus, 208/120V 3 phase 4W, MLO (Main Lug Only)
MSB Feeder breakers:
1) 2500A CB to Fire Pump controller.
2) 800A CB to Residential meter banks RMB1
3) 1000A CB to Residential meter banks RMB2
4) 1000A CB to Residential meter banks RMB3
5) Meter + 600A CB to Commercial tenant 1
6) Meter + 400A CB to Commercial tenant 2
7) Meter + 200A CB to Commercial tenant 3
8) Meter + 2500A CB to House panel.
I don’t think there’s a violation of 230.71 (Six disconnect rule) for the 4000A MLO Main service switchboard MSB but I wonder if there’s a violation of 230.71 (Six disconnect rule) for the RMB1, RMB2, RMB3:
RMB1, RMB2, RMB3 are MLO switchboards and each of them a) feeds at least 7 residential units, b) has at least 7 residential meters and c) not in the same room with the 4000A MSB.
Can permanent labels be added at the MLO switchboards RMB1, RMB2, RMB3 to inform the firefighters (in case there a fire at the residential units) that the breakers shutting down the residential meter bank switchboards are at MSB two floors down from where the firefighters are?
Thanks.
Thanks.