Roger Stevenson
- 2974 Copperopolis, Ca
- Electrical Contractor since 1978
What is the minimum wire size required by NEC for a A/C mini split system with a minimum 18.5 amp and Maximum 25 amp over current protection?
Yes 14-2 romexDo you mean a MCA of 18.5 and a max OCPD of 25 as stated on the label? If so the conductors could be #14 using 75 degree conductors (pipe and wire) of if using NM cable they would need to be #12 as NM must use the 60 degree ampacity.
MCAWelcome to the forum.
What size wire, of the type (NM, MC, THWN, etc.) you intend to use is rated at 18.5a or better?
We usually don't like to just answer such questions, preferring to teach you how to figure it out.
Added: Is that 18.5a the MCA or minimum breaker?
The * in the ampacity table sends you to 240.4(D), the small conductor rule. The parent text says the rules in 240.4(E) or (G) can override the small conductor rule. The rule in 240.4(G) says that the conductor sizing and overcurrent protection rules in Article 440 apply to air conditioning circuits.Doesn’t #14 Copper have an asterisk and footnote requiring 15 amp breaker maximum and #12 20 amp breaker Maximum and #10 30 amp max?
Yes 14-2 romex
So 14-2 Romex is allowed on a 20 amp breaker?The * in the ampacity table sends you to 240.4(D), the small conductor rule. The parent text says the rules in 240.4(E) or (G) can override the small conductor rule. The rule in 240.4(G) says that the conductor sizing and overcurrent protection rules in Article 440 apply to air conditioning circuits.
14-2 NM cable is limited to 15 amps of MCA.So 14-2 Rolex is allowed on a 20 amp breaker?
That's correct. The MCA would be a maximum of 15 amps but the OCPD could be any size on the nameplate.Yes, if it feeds a motor, HVAC unit, or some of the other exceptions. The MCA would need to be 15A or less though.
No the MCA is 18.5Yes, if it feeds a motor, HVAC unit, or some of the other exceptions. The MCA would need to be 15A or less though.
Then you cannot use #14 AWG NM cable.No the MCA is 18.5
No, 12-2 Romex.Yes 14-2 romex
Only if the MCA was 15a or lower.So 14-2 Romex is allowed on a 20 amp breaker?
No the MCA is 18.5
Thank youThen you cannot use #14 AWG NM cable.