Supply side and Backfeed ( 2 Point of interconnection)

Status
Not open for further replies.

msi99

Member
Location
Texas
Occupation
Solar
If the property already has an existing enphase system hooked up as a line side, can we add a solar edge system to the property via a back feed if the 120% rule is satisfied?
 
Sure, if the AHJ is OK with two points of interconnection on the service. The supply side connection did not change anything in the panel.
 
The only other thing is that the combined output of the systems can't exceed the service rating. Which is probably unlikely anyway.
Right; I didn't think of that but as you say, for residences the PV output not very likely to approach that limit.
 