Doc13067
Senior Member
- Location
- Bucks County/Philadelphia, PA USA
If I’m installing two 200A services in one structure can I run one length of #4 cu to the water pipe from each main disconnect? Or would I have to either run two lengths of #4 (one from each service) or size it to 1/0 cu if I wanted to run one length? This was originally one 400A service but the poco preferred we split it into two separate taps and make it 200/200.
If I have to make it 1/0 if I want one GEC to serve both services my next question is going to be how to get a wire that size onto a 1 inch water pipe.
If I have to make it 1/0 if I want one GEC to serve both services my next question is going to be how to get a wire that size onto a 1 inch water pipe.