Tcouillard
Member
- Location
- New Hampshire
- Occupation
- Electrician
I need a #10 wire for a residential AC unit looking to see if I need to run 10-3 or 10-2? Also GFCI protected or standard 240v breaker.
What's the nameplate MCA?It’s 240v unit
A lot of misunderstanding out there, and MCA is what determines conductor ampacity needed. Lots of units connected with 10 AWG out there that code will actually allow to be connected with 12 AWG. Not a violation to use 10, just something that can be done and should normally cost less to do.What's the nameplate MCA?
I would presume these also have their own disconnecting means in the unit and the service receptacle is somehow connected ahead of that? Otherwise it wouldn't comply with 210.63 requirements.I don't know about residential sizes, but commercial RTUs have their own service recpt built in these days.
I don't know about residential sizes, but commercial RTUs have their own service recpt built in these days.
It can't be connected to load side of the disconnecting means at the unit. It is not prohibited from being connected to the HVAC branch circuit but you will need a neutral in the circuit and will need additional overcurrent protection if the HVAC circuit is not 15 or 20 amps.I just read 210.63 no wonder I have not seen it. Can’t be connected off the hvac branch circuit.
Now I feel dumber for saying my first post