Thank you for taking the time to review this.
We have several discrete signal and serial cables that are snaking around a machine located in a Class 1 Div 2 area. The machine supplier would like to use P clamps and structure to support the cable and not cable tray or conduit due to the routing. From 725 Industrial Locations, it looks like the cable can be outside of tray or transitioning between tray a maximum of 6'.
Is it accurate that the cable, which is over 20 feet can not use P clamps or similar support every 6', it must be in tray to protect the cable. The 6' is to transition from tray to tray or tray to enclosure?
Second question is, many sensor manufacturers such as Rockwell or Turk provide a cable for the device either integral or connectorized and recommends the cable on the control drawing. The sensor cables are not marked, are they assumed PLTC, ITC, something else? What are the installation rules if something else?
Thank you
Thank you